Well, EMT isn't allowed in a Class 1 Div 2 area per 501.4(B), assuming that this is power wiring not exempted under 501.4(B)3.

If the conduit is rigid or IMC, then the use of EMT connectors on it would be a violation of listing requirements under 110.3(B).