OK...I'm going to take a stab at this. I can't quote the NEC reference.
#1. Inadequate working clearance in front of equipment likely to be serviced.
#2. 1 laundry recepticle is required and does not need to be GFCI protected. The second duplex needs GFCI protection. If it is protected by a GFCI breaker then it needs to have the yellow tag stating such.
#3. Water pipes occupying the area directly above the service panel.
#4. No bonding jumper at the water meter.
#5 Panel on the side has wires that are not protected.
#6 Inadequate conductor size for the water heater. No protection also. It looks like 14 gage NM cable.
#7. Flying splices in the drop ceiling.
#8. No covers on the boxes.
#9. Too many conductors in the romex connector at the jbox.
#10. Cover screw missing from the loadcenter.

#11. Nutdriver left on the washing machine.(OK, Just kidding)

Wow, now i'm tired.

Blessings and GOD Bless America
Mark Randazzo