Bob,
I don't see any exposed GEC. It appears to be in PVC condiut to me. Around here when the GEC is in PVC, there is no exposed GEC as the PVC is terminated below grade.
But beyond that how would an EC know where the cable company will need this connection considering the electric service was installed years before cable TV was brought to the house?
This service look fairly new and the code rule requiring an accessbile intersystem grounding connection point has be in the code for 3 or 4 code cycles. The code section only requires that this connection point be provided at the service equipment and at the service disconnect. Maybe, it really isn't required at this location, because I don't think that the meter is service equipment.
Don