I have a question about bonding.

I went to a house and had to replace a receptacle because it was damaged.

It was a 2 prong type supplied by armoured cable that had no bonding conductor. The box was bonded by the armour on the BX.

I decided to change this old receptacle with a GFCI type because of no bonding conductor in the box and the armour of the BX is not suitable for bonding.

I have been looking in my code book on this matter.

CEC 26-700(7)(a) states that if I was to replace it with a 3 prong I could bond it to the cable sheath if the sheath is already bonded to ground.

I think that the armour on BX is not a sheath but is cable armour, because in the code it is always referred to as armour, so it can’t be used as a bonding method.

• Is my understanding of 26-700(7)(a) your interpretation or do you have another?

Any comments?