Ares,
These tables were computed based on the IEEE 835.
To determine underground cable ampacities, refer to the IEEE Standard #835, "Standard Power Cable Ampacities".
If the installation is exactly as illustrated in Diagrams B4-1 to B4-4 of Appendix B, use Tables D8A - D11B and D13A - D16B of Appendix D.
Tony Moscioni
Electrical Inspector
Electrical Safety Authority