Under no circumstances shall a generator be connected to any portion of a wiring system except where it is connected through a transfer device that makes it impossible for the generator to feed back into the normal power supply. [Ontario Electrical Safety Code (OESC) 6-106, 14-612, 75-612].


Where a double throw transfer device is mounted at a service entrance, the transfer device shall be located on the load side of the service entrance switch [OESC 75-612 (3)(

It was my intent to mount a proper transfer switch on the load side of the main disconnect.

From all the rest I gather that the neutral should also be switched in my case.

Now can you reccommend a brand of switch?