This thread is NEC and other codes so let me offer a CEC solution .
Section 28 sizes multiple motor circuits as 1.25 time the largest motor plus the sum of the currents of other motors that would run at the same time or 17.575 amps. For motors this is fine on #12 but the breaker could be undersized if both motors start at the same time. Not a violation here.