I find with Reno

430.6(A) (1) Table Values. Other than for motors built for low speeds (less than 1200 RPM) or high torques, and for multispeed motors, the values given in Table 430.247,
Table 430.248, Table 430.249, and Table 430.250 shall be used to determine the ampacity of conductors or ampere ratings
of switches, branch-circuit short-circuit and ground-fault protection, instead of the actual current rating marked on the
motor nameplate.
_____________________________________________

The conductors are sized at 125% or greater regardless of whether it is a continuous load or not
_____________________________________________

The nameplate rating is used for sizing separate overcurrent protection


[This message has been edited by electure (edited 03-04-2007).]