Redsy,
Don't forget Weatherproof-in-use cover(s), Make sure that Pump cord is 12 ga and 3ft maximum, and you might want a switch or Timeclock out there to control the Pump receptacle. If bonding lugs will be buried make sure they are rated for direct burial.
BTW, If you put GFCI protection before wiring goes underground you can save yourself 6 inches of digging (see Table 300.5 Column 4).
I think that about does it, assuming no overhead wiring nearby, or additional metal objects nearby that must be bonded.
Bill