George, if you read up this thread a little ways, you'll see that even though a GEC is required for the garage, it doesn't need to be located at the garage, and can share the house rod.

250.64(C)(3) permits connections to busbar to be used vice a single continuous conductor. The grounding conductor run between the house and garage, and house's GEC thus satisfy 250.32.