The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
1 registered (Tony Moscioni), 213 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#84583 - 04/11/03 10:43 PM running romex outdoors
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Is there any problem with running romex up under an eve of a home as long as it is out of the weather and not subject to mechanical damage?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
2014 / 2011 NEC & Related Books and Study Guides
#84584 - 04/11/03 10:47 PM Re: running romex outdoors
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
no it is not good idea to run romax for any outdoor appaction the uf wire will be better useage due it say for underground and sunlight restent and i am sure the ahj inspecter will say just use the uf wire other wise run in the conduct with twhn wire as need i am sure few other sparky will say the same answer what i say

merci marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#84585 - 04/12/03 02:34 AM Re: running romex outdoors
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
They still build residential garages with exposed studs and romex run in them and thats just as much outdoors.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#84586 - 04/12/03 04:06 AM Re: running romex outdoors
zapped208 Offline
Member

Registered: 02/18/03
Posts: 201
Loc: Somewhere in USA
Uses not permitted for NM cable, 334.12(A)(10)d, "Where exposed or subject to excessive moisture or dampness".
_________________________
Shoot first, apologize later.....maybe

Top
#84587 - 04/12/03 04:29 AM Re: running romex outdoors
spyder Offline
Member

Registered: 10/14/02
Posts: 211
Loc: Massachusetts
Run it in UF.