Posted By: aldav53 running romex outdoors - 04/12/03 05:43 AM
Is there any problem with running romex up under an eve of a home as long as it is out of the weather and not subject to mechanical damage?
Posted By: frenchelectrican Re: running romex outdoors - 04/12/03 05:47 AM
no it is not good idea to run romax for any outdoor appaction the uf wire will be better useage due it say for underground and sunlight restent and i am sure the ahj inspecter will say just use the uf wire other wise run in the conduct with twhn wire as need i am sure few other sparky will say the same answer what i say

merci marc
Posted By: aldav53 Re: running romex outdoors - 04/12/03 09:34 AM
They still build residential garages with exposed studs and romex run in them and thats just as much outdoors.
Posted By: zapped208 Re: running romex outdoors - 04/12/03 11:06 AM
Uses not permitted for NM cable, 334.12(A)(10)d, "Where exposed or subject to excessive moisture or dampness".
Posted By: spyder Re: running romex outdoors - 04/12/03 11:29 AM
Run it in UF.