#79639 - 01/09/02 01:17 PM multi-outlet surge protectors
whitaker Offline
Junior Member
Registered: 01/09/02
Posts: 1
Loc: FORT SCOTT, KS USA
Recently I was asked if multi-outlet surge protector extension cords are legal as a permanent power source. My initial reaction was no since they are still an extension cord, but I can't find the section in the 1997 NEC that applies. Section 240-4 doesn't address this product.

Thanks for all your help!!!
_________________________
LISA WHITAKER
CITY OF FORT SCOTT, KS
Top
2017 / 2014 NEC & Related Books and Study Guides
#79640 - 01/09/02 09:54 PM Re: multi-outlet surge protectors
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
Here's a start. 210-50(b) says that a receptacle outlet shall be installed wherever flexible cords with attachment plugs are used. I looked under 400 (Flexible cords and cables) and noted 400-7(b) which requires cord and plug appliances and equipment to be energized from a receptacle outlet. Looking under "receptacle outlet" and "receptacle" in definitions of Art 100 we see that they are talking about receptacles on a yoke..which pretty much rules out your power strips.
There is some language in 410-56(g),that actually pertains to the context of fixture wiring but might be repeated somewhere else in the Code, that: "No receptacle shall be installed so as to require an energized attachment plug as its source of supply."
Top
#79641 - 01/10/02 04:17 PM Re: multi-outlet surge protectors
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
whitaker,

Take a look on the back of the strip. chances are that is says the word 'Temporary' somewhere, which would probably also be a condition of it's UL listing.

Bill
Top
#79642 - 01/10/02 07:30 PM Re: multi-outlet surge protectors
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
Whit
Where did you get that 1997 NEC anyway? I don't think we got that one down here.
Top
#79643 - 01/11/02 04:30 AM Re: multi-outlet surge protectors
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
These things are used extensively around here. The Fire Depts here don't seem to consider them an extension cord, as they don't write them up in their inspections.
As a "temporary", does that mean they must be unplugged and plugged back in once every 90 days?
Top
#79644 - 01/11/02 06:10 AM Re: multi-outlet surge protectors
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
The one I have in front of me says on the back "Temporary Power Tap" and the UL sticker says; "Listed Relocatable Power Tap"

I do unplug it ocassionally during storms or vacations, but no, not every 90 days
(don't send Joe's 'Enforcer Guy' after me!)

Bill

[This message has been edited by Bill Addiss (edited 01-11-2002).]
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals