The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
2 registered (HotLine1, Webmaster), 0 Guests and 207 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77637 - 06/29/01 05:15 PM transformer grounding
dom Offline
Junior Member

Registered: 06/29/01
Posts: 8
When installing a 75kva dry type transformer,
(480delta-120/208wye) If using a water pipe as a ground electrode, does it need to be supplemented by another electrode? Would an equipment ground installed with the primary circuit feeding the transformer qualify as a supplementary ground electrode? thanks

Top
2017 / 2014 NEC & Related Books and Study Guides
#77638 - 06/29/01 05:28 PM Re: transformer grounding
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Hi dom!

450-10>>>250-20(d)>>>250-30(a)(2)

a start..


Top
#77639 - 06/30/01 04:19 PM Re: transformer grounding
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
dom,
If the transformer feeder originates in the building service equipment, you can install the GEC in with the feeder conducotrs. See the exception in 250-30(a)(3).
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#77640 - 07/02/01 05:24 PM Re: transformer grounding
dom Offline
Junior Member

Registered: 06/29/01
Posts: 8
Is there a different requirement for the ground electrode for the main switchgear(250-50) and a ground electrode at a transformer fed from a subpanel in the same system?(250-30(b)(2).- 250-30(a)(3).
thanks