The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77637 - 06/29/01 05:15 PM transformer grounding
dom Offline
Junior Member

Registered: 06/29/01
Posts: 8
When installing a 75kva dry type transformer,
(480delta-120/208wye) If using a water pipe as a ground electrode, does it need to be supplemented by another electrode? Would an equipment ground installed with the primary circuit feeding the transformer qualify as a supplementary ground electrode? thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#77638 - 06/29/01 05:28 PM Re: transformer grounding
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Hi dom!

450-10>>>250-20(d)>>>250-30(a)(2)

a start..


Top
#77639 - 06/30/01 04:19 PM Re: transformer grounding
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
dom,
If the transformer feeder originates in the building service equipment, you can install the GEC in with the feeder conducotrs. See the exception in 250-30(a)(3).
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#77640 - 07/02/01 05:24 PM Re: transformer grounding
dom Offline
Junior Member

Registered: 06/29/01
Posts: 8
Is there a different requirement for the ground electrode for the main switchgear(250-50) and a ground electrode at a transformer fed from a subpanel in the same system?(250-30(b)(2).- 250-30(a)(3).
thanks