When installing a 75kva dry type transformer,
(480delta-120/208wye) If using a water pipe as a ground electrode, does it need to be supplemented by another electrode? Would an equipment ground installed with the primary circuit feeding the transformer qualify as a supplementary ground electrode? thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#77638 06/29/01 08:28 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Hi dom!

450-10>>>250-20(d)>>>250-30(a)(2)

a start..

[Linked Image]

#77639 06/30/01 07:19 PM
Joined: Nov 2000
Posts: 2,148
R
Member
dom,
If the transformer feeder originates in the building service equipment, you can install the GEC in with the feeder conducotrs. See the exception in 250-30(a)(3).
Don(resqcapt19)


Don(resqcapt19)
#77640 07/02/01 08:24 PM
Joined: Jun 2001
Posts: 8
D
dom Offline OP
Junior Member
Is there a different requirement for the ground electrode for the main switchgear(250-50) and a ground electrode at a transformer fed from a subpanel in the same system?(250-30(b)(2).- 250-30(a)(3).
thanks