#77637 06/29/01 08:15 PM
dom Offline OP
When installing a 75kva dry type transformer,
(480delta-120/208wye) If using a water pipe as a ground electrode, does it need to be supplemented by another electrode? Would an equipment ground installed with the primary circuit feeding the transformer qualify as a supplementary ground electrode? thanks
#77638 06/29/01 08:28 PM
Hi dom!
450-10>>>250-20(d)>>>250-30(a)(2)
a start..
#77639 06/30/01 07:19 PM
dom,
If the transformer feeder originates in the building service equipment, you can install the GEC in with the feeder conducotrs. See the exception in 250-30(a)(3).
#77640 07/02/01 08:24 PM
dom Offline OP
Is there a different requirement for the ground electrode for the main switchgear(250-50) and a ground electrode at a transformer fed from a subpanel in the same system?(250-30(b)(2).- 250-30(a)(3).
thanks
