#207385 - 10/23/12 07:55 PM 230-2
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
230-2 states that a structure shall be supplied by only one service. We have an existing commercial building with two services on it. One service supplys the building to which the services are attached, the second service supplys a pedestal on an adjacent property. Both parcels are owned by the same company. The AHJ is refusing a re-connect stating 230-2. I don't see where 230-2 applies, the second service is supplying another structure (the pedestal, it is not supplying the same building as the first service. We do not have two services supplying one building.

Also, 230.3 states service conductors supplying a building or other structure shall not pass thru the interior of another building or structure. The load side conductors of the second service do pass thru the first building, but they are not "service conductors", correct?

Top
2017 / 2014 NEC & Related Books and Study Guides
#207386 - 10/23/12 10:19 PM Re: 230-2 [Re: BigB]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Where are the service disconnects?
_________________________
Greg Fretwell
Top
#207387 - 10/23/12 10:33 PM Re: 230-2 [Re: gfretwell]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Originally Posted By gfretwell
Where are the service disconnects?


They are both on the first building, side by side.
Top
#207388 - 10/23/12 11:41 PM Re: 230-2 [Re: BigB]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Then I say there are 2 services brought to one building, sorry.
Maybe you can get a vote the other way here but the only one that counts is your AHJ.
_________________________
Greg Fretwell
Top
#207391 - 10/24/12 08:08 AM Re: 230-2 [Re: BigB]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Are there two (2) utility drops? IF there is one utility drop, or one UG lateral then IMHO it sounds like only one service.
_________________________
John
Top
#207401 - 10/24/12 07:06 PM Re: 230-2 [Re: HotLine1]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Originally Posted By HotLine1
Are there two (2) utility drops? IF there is one utility drop, or one UG lateral then IMHO it sounds like only one service.


Of course, I wasn't thinking since I was pissed off from dealing with the local bureaucracy. There is only one service, just two meter mains. Since I didn't show the drop on my drawing they probably thought there were 2 drops, or else they are just being stupid, and it is rubbing off on me. I will let you know what happens when I point this out. Thanks.


Edited by BigB (10/24/12 07:08 PM)
Top
#207404 - 10/24/12 07:31 PM Re: 230-2 [Re: BigB]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
OK you are right, one service, 2 disconnects and a second building scenario.

It sounds like you just resubmit your plans, say sorry for the confusion and move on. wink
_________________________
Greg Fretwell
Top
#207406 - 10/24/12 07:51 PM Re: 230-2 [Re: BigB]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Part of the problem is our new permit application system, we are using ProjectDox. It is nice in some ways that you can do everything from the office but like everything else on the internet it's not always the same as face to face.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals