#174806 - 02/14/08 05:15 AM Another 08,Pool issue
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
680.26 (C) Pool water......

States water must be bonded.. Now the pump I don't feel is in "Direct contact" with the water, Gaskets,seals,impeller etc.

So, now we do the 9 sq inch thing.

Does the light trim count? Wet niche of course would.
My thought woud be to install a peice of stainless pipe in 1 of the lines. This seems to be an easy solution.

The season (here) is approaching, so thoughts would be great.

Lee



Edited by leland (02/14/08 05:16 AM)
Top
2017 / 2014 NEC & Related Books and Study Guides
#174817 - 02/14/08 08:21 AM Re: Another 08,Pool issue [Re: leland]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
A 2" metallic pipe nipple on the pump with a suitable clamp would meet the requirement, even with 1.5" pipe. (9.42 sq/in)

Most of the wet niches I see around here are PVC but there usually is a metal ring on the light. You would also be able to include a metal ladder or even the ladder cups if they are metal and under water.
_________________________
Greg Fretwell
Top
#174825 - 02/14/08 04:15 PM Re: Another 08,Pool issue [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Greg:
Today's discussion regarding the ladder....
Pools here are closed for the winter, and the ladders are removed for the cover.
Based on that, the water bond is not there with the ladder out.
Comments??
_________________________
John
Top
#174828 - 02/14/08 06:57 PM Re: Another 08,Pool issue [Re: HotLine1]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
YA, What Hotline1 said.

We don't all live in the sunshine state!! Haven't seen sun in 5 looong days!! Damn cold too!!

(all in jest- can't (don't know how) to find the icons)

Now the next step is to find (or make) an approved nipple with a lug on it.
Top
#174835 - 02/15/08 04:17 AM Re: Another 08,Pool issue [Re: leland]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
If steel rebar is considered a grounding electrode when of sufficient length in contact with concrete, wouldn't the pool water also be considered grounded by contact? Or does the liner completely negate that?
Top
#174858 - 02/15/08 03:02 PM Re: Another 08,Pool issue [Re: SteveFehr]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Steve, the issue they are talking about is a plastic pool, double insulated pump and all plastic nicheless light. If you have no other way to bond the water the 2008 requires some other piece of metal 9 sq/in to accomplish it.
John
If the ladder is out, the cups are still going to be there.
_________________________
Greg Fretwell
Top
#174878 - 02/16/08 07:17 AM Re: Another 08,Pool issue [Re: gfretwell]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
Originally Posted By gfretwell
John
If the ladder is out, the cups are still going to be there.


Greg, these cups are not typicaly in contact with the water are they? My pool has the drop in ladders, cups only in the deck, (In ground liner). No hand rail at the steps,though I suppose if there were one that would cover it.

I think we will see a metalic coupleing,as discussed, arive shortly.This would be a nice convieniant and standard solution.
Top
#174884 - 02/16/08 09:24 AM Re: Another 08,Pool issue [Re: leland]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I am not really sure how many "plastic only" pools there are in the US. Concrete "in ground" is the norm here and the rebar makes this an excellent ground plane. The sun tears up plastic and I don't think I have ever seen the vinyl liner pools here except a few above ground. Usually they either go for a concrete pool or they abandon the pool idea altogether
_________________________
Greg Fretwell
Top
#174896 - 02/16/08 03:09 PM Re: Another 08,Pool issue [Re: gfretwell]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Greg,

Up here I have seen in the last 9 years at least 7 plastic pools. I am not a big fan of these pools, but I have to inspect them. BTW, these pools are the only ones that I have seen problems with "Stray Voltage". The concrete or steel w/plastic liners never had any stray voltage ( to my knowledge) problems around here.

John, If the the ladder is out for the winter, is the pool bonding that critical? smile LOL, I mean is anyone going to swim up here in Jan? Today was a balmy 25-35 deg and sunny, a nice day for a walk, but not a swim.

Top
#174899 - 02/16/08 03:30 PM Re: Another 08,Pool issue [Re: harold endean]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Harold:
My thoughts went down that road...
Metal ladder connected mechanically to bonded cups. OK as a "water bond".
I thought that would be an acceptable solution.....
Comment was...'no good because ladder is removed when pool is covered' (winterized)
My reply was...'who would/could be affected in any way by a covered/winterized pool?'
Comment was to the effect that the install would not be code compliant.

Debate will continue at a future date.
_________________________
John
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals