OP
As far as I know, a GFI ckt is not required for any type of water heater under a sink, correct?
The Golden Rule - "The man with the gold makes the rule"
If we are talking residential you are correct.
Roger
[This message has been edited by Roger (edited 08-18-2005).]
Wait a minute...Under the 2002 I agree with Roger 100%. Under the 2005, however, it would be required, unless the sink is located in a kitchen, as per 210.8(A)(8).
Ryan Jackson, Salt Lake City
Ryan, did you mean 210.8(A)(7) of 2005? And yes, I was using 2002 in my reply Roger
Sorry roger, thats what I get for not looking up my references!
Ryan, why would GFCI protection be required? 210.8 only applies to 15 and 20 amp 125 volt receptacles.
Curt
Curt Swartz
Hello Curt, I was assuming a cord and plug connected unit and think Ryan was as well.
Roger
OP
This is at our church a commercial building. Its a 30 amp 120 volt circuit.
Not required for a 30 amp circuit.
Posts: 5,445 Likes: 3
Cat Servant Member
At last! I found it!
Last 12/28/04, I posted a pic of this in the "Photos for Discussion" forum. The last comment was on 1/10/05.
Look for thread titled "GFCI- needed here?"