As far as I know, a GFI ckt is not required for any type of water heater under a sink, correct?
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
If we are talking residential you are correct.
Roger
[This message has been edited by Roger (edited 08-18-2005).]
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Wait a minute...Under the 2002 I agree with Roger 100%. Under the 2005, however, it would be required, unless the sink is located in a kitchen, as per 210.8(A)(8).
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Ryan, did you mean 210.8(A)(7) of 2005? And yes, I was using 2002 in my reply Roger
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Sorry roger, thats what I get for not looking up my references!
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
Ryan, why would GFCI protection be required? 210.8 only applies to 15 and 20 amp 125 volt receptacles.
Curt
Curt Swartz
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Hello Curt, I was assuming a cord and plug connected unit and think Ryan was as well.
Roger
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
This is at our church a commercial building. Its a 30 amp 120 volt circuit.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Not required for a 30 amp circuit.