#77830 07/16/01 06:47 PM
Steve T Offline OP
Is it acceptable to run LV conductors in the same conduit with the regular voltage conductors.
For instance, undercabinet lighting with the xfmrs in the basement, run to a kitchen above in EMT with the 120v conductors.
I don't think anything is wrong with it, provided the insulation is rated for the highest voltage on all the conductors.
Any opinions?
#77831 07/16/01 07:35 PM
no Opinion Steve, just confusion, would we need to go to 725-26?
#77832 07/16/01 07:51 PM
See Section 300-3(c) Conductors of Different Systems.
[This message has been edited by Joe Tedesco (edited 07-20-2001).]
#77833 07/16/01 08:52 PM
Yes yes,
but i think the original Q was to address Low-V , as in after a 120/12V X-former. Inasmuch as there is no definition of LV.
#77834 07/17/01 08:13 AM
Sounds like he is putting the ballast for a light fixture in the basement. Check the xfmrs secondary output voltage. It may be higher than you think. Of course, if the xfmr is truly a step down version, then as pointed out by Joe Tedesco, all the conductors in the same raceway, enclosure, or cable must be insulated for the highest voltage.
#77835 07/18/01 08:18 PM
http://www.iaei.com/ubb/Forum1/HTML/000376.html
well Steve, this should be interesting!