mixed voltages - 07/16/01 10:47 PM
Is it acceptable to run LV conductors in the same conduit with the regular voltage conductors.
For instance, undercabinet lighting with the xfmrs in the basement, run to a kitchen above in EMT with the 120v conductors.
I don't think anything is wrong with it, provided the insulation is rated for the highest voltage on all the conductors.
Any opinions?