ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 516 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
Can someone explain a couple of things to me on this nameplate info for a convection oven:

TOTAL KW = 5.5KW

208, 240v 3 Phase Loading - KW per Phase:
L1-L2 = 2.5, L2-L3 = 0 , L1-L3 = 3Kw

Nominal Amps per line wire:
3 Phase 208 Volt
L1 =23, L2= 10, L3=12

Why is there unbalanced loads per phase and how would you choose a cable wire size with all the different amperages? Would you base cable wire size on the largest - 23 amps? Would you use a 3 pole 30 amp breaker?

Joined: Jan 2003
Posts: 4,391
I
Moderator
The unbalanced current is the result of single phase fan motors and controls.

Yes you must select a cord and branch circuit with at least a 23 amp capacity.

[This message has been edited by iwire (edited 04-02-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
L2-L3 = 0 kw...why no load b/w 2 and 3?

[This message has been edited by Cinner (edited 04-02-2006).]

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
With no load between L2-L3 it would be very easy to convert the oven to work on a 2 wire single phase supply.

Joined: Dec 2004
Posts: 78
C
Cinner Offline OP
Member
would a 3 pole 30 amp breaker be sufficient?


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5