drgnz23 Offline OP
Okay I work in a laboratory enviroment where i have to install two new receptacles in a room. Is it legal to run flex down the wall or do i have to run EMT? Maybe about forty feet long? Please help
#56512 09/23/05 12:46 PM
Not a Code violation unless exposed to physical damage.
Also refer to Section 250.118(6) Lengths over six feet MUST have a grounding conductor.
Alan--
Alan--
If it was easy, anyone could do it.
#56513 09/23/05 02:27 PM
drgnz23 Offline OP
Always run a grounded conductor.
Just having a discussion with my leadman and he thinks we should run EMT in walls. Without ripping away walls Flex should be legal to run. He swears that in our enviroment flex shouldnt be used. I cant find anything that says we cant.
#56514 09/23/05 04:15 PM
EMT (Thinwall) is allowed to be fished without couplings.
358.30(A)
Exception No. 2: For concealed work in finished buildings or prefinished wall panels where such securing is impracticable,
unbroken lengths (without coupling) of EMT shall be permitted to be fished.
#56515 09/23/05 10:36 PM
How exactly is the EMT supposed to be held together without couplings?
~Peter
#56516 09/23/05 11:13 PM
EMT is 10' long top plate to bottom plate(wall interior) is less than 8' no coupling concealed.
bill