Posted By: drgnz23 flexible metal conduit - 09/23/05 03:33 PM
Okay I work in a laboratory enviroment where i have to install two new receptacles in a room. Is it legal to run flex down the wall or do i have to run EMT? Maybe about forty feet long? Please help
Posted By: Alan Nadon Re: flexible metal conduit - 09/23/05 04:46 PM
Not a Code violation unless exposed to physical damage.
Also refer to Section 250.118(6) Lengths over six feet MUST have a grounding conductor.
Alan--
Posted By: drgnz23 Re: flexible metal conduit - 09/23/05 06:27 PM
Always run a grounded conductor.
Just having a discussion with my leadman and he thinks we should run EMT in walls. Without ripping away walls Flex should be legal to run. He swears that in our enviroment flex shouldnt be used. I cant find anything that says we cant.
Posted By: Joe Tedesco Re: flexible metal conduit - 09/23/05 08:15 PM
EMT (Thinwall) is allowed to be fished without couplings.

Quote
358.30(A)

Exception No. 2: For concealed work in finished buildings or prefinished wall panels where such securing is impracticable,
unbroken lengths (without coupling) of EMT shall be permitted to be fished.
Posted By: Peter Re: flexible metal conduit - 09/24/05 02:36 AM
How exactly is the EMT supposed to be held together without couplings?
~Peter
Posted By: electricbill Re: flexible metal conduit - 09/24/05 03:13 AM
EMT is 10' long top plate to bottom plate(wall interior) is less than 8' no coupling concealed.
bill