I have an existing main panel that has the water meter under it about 2ft below and it's off the wall 10 inches. Inspector says to move the panel as the code says it can't be mounted above the water meter. I didn't see it so here I am asking. Thanks.
|
|
|
|
Joined: Sep 2004
Posts: 37
Member
|
Clearence area for Panel is 24" to sides 36" to front from ground to Panel
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
110.26 covers clearances about panels. There are two parts: the working clearance in front (30 x 36) and the dedicated space above and below (equal to the footprint from floor to ceiling).
Earl
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
It is a violation of 110.26 (3), but You say it is an existing situation
What type of authority does this inspector have that he can have you change an existing condition, or what type of project are we talking about?
Roger
|
|
|
|
Joined: Oct 2003
Posts: 259
OP
Member
|
I am changing out the panel to a new panel, thats it.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Joey, the inspector has a valid stance.
Roger
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
File under "why people avoid permits". Tough to say without seeing how obsructed the panel is but I do service upgrades like this all the time and never have I moved the panel location. Burdening the homeowner with an added cost might not be an option for them. Thus they will do nothing or avoid permits altogether. Rule 3 from Mass Elec Code. "Addtions or modifications to an existing installation shall be made in accordance with this Code without bringing the remaining part of the installation into compliance with the requirements of this Code. The installation shall not create a violation of this Code, nor shall it increase the magnitude of an existing violation." Where does this leave us?
|
|
|
|
Joined: May 2004
Posts: 697
Member
|
If it were anything but a water meter I'd suggest that the plumber violated the code and needed to move the plumbing. That's the position some VERY NICE inspectors have taken in the past. It really shouldn't be too much work to relocate to one side with a 90 degree sweep.
Dave
|
|
|
|
Joined: May 2004
Posts: 697
Member
|
...or add a couple floor-to-ceiling 2X4s and bring the panel away from the wall a foot or two with a long RMC nipple.
Dave
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Dave moving the panel is obviously easy. What about all the airing that has to go back into it. Not likely that it will reach.
|
|
|
Posts: 61