1 members (Scott35), 520 guests, and 39 robots.
#47124 01/10/05 08:19 PM
Coastal Offline OP
Is there a special switch or circuit breaker made and/or required for HID lighting or is a standard 20 Amp switch all that is necessary? I have 700 va of Metal Halide and 400 va of Mercury Vapor on a dedicated 20 amp circuit.
#47125 01/10/05 08:24 PM
Coastal, see 240.83(D) concerning the breaker.
As fas as a snap switch, it would only be necessary to be rated for the load.
Roger
#47126 01/13/05 07:40 PM
From what I gather from 240.83, if the lighting loads go through a lighting contactor or other switch, the HID or SWD breakers are not nessasary.
Is this correct?
#47127 01/13/05 07:56 PM
Dnkldorf,
Is this correct?
that is the way I read it too.
Also notice that there is no other mention of a "listed breaker" in 240. [Linked Image]
Roger
