Posted By: Coastal HID Switching and/or OCP - 01/11/05 12:19 AM
Is there a special switch or circuit breaker made and/or required for HID lighting or is a standard 20 Amp switch all that is necessary? I have 700 va of Metal Halide and 400 va of Mercury Vapor on a dedicated 20 amp circuit.
Posted By: Roger Re: HID Switching and/or OCP - 01/11/05 12:24 AM
Coastal, see 240.83(D) concerning the breaker.

As fas as a snap switch, it would only be necessary to be rated for the load.

Roger
Posted By: Dnkldorf Re: HID Switching and/or OCP - 01/13/05 11:40 PM
From what I gather from 240.83, if the lighting loads go through a lighting contactor or other switch, the HID or SWD breakers are not nessasary.
Is this correct?
Posted By: Roger Re: HID Switching and/or OCP - 01/13/05 11:56 PM
Dnkldorf,
Quote
From what I gather from 240.83, if the lighting loads go through a lighting contactor or other switch, the HID or SWD breakers are not nessasary.
Is this correct?

that is the way I read it too.

Also notice that there is no other mention of a "listed breaker" in 240. [Linked Image]

Roger