565
35
... Anyone here know if ya can sleeve NM in conduit..? I've been doing it for years,and terminating it with a "from-to" for 1/2"EMT..There was a buzz going around at my supply house about this, and although I checked the "Good Book" about it, I can't find a reference....
Please elaborate on your term "sleeve". When I picture a sleeve, I picture a piece of conduit about 6"-12" long. This would be fine. If you are thinking more than 10', this may be a different story.
Ryan Jackson, Salt Lake City
These installations could be anywhere from 30" to 60" usually done in unfinished basements, where a receptacle is needed, and I'm coming down from above..ie; the floor joists...and mounted on the foundation wall. I've also done it when "poking thru a floor to run a receptacle to a 4" square (1900) box
[This message has been edited by Attic Rat (edited 12-15-2003).]
334.15(B) discusses using a raceway as a means of protection from physical damage. I think that fits your description. You should be fine.
Thanx Ryan, I thought so, but I wasn't sure..
Any time. Don't be a stranger just because your question got answered. The is much to be learned here. See ya around
This may be a dumb question, but what on earth is a "from-to"?
...it's an EMT female fitting, with a set-screw on one end and a romex-like connector on the other end....only made in 1/2", and 3/4"...
OK, I just never heard them called that. Thanks
Attic Rat, Nice to have you here. 1900's and "from-to's". You must be from the NY area. Your description is exactly how I do it. Never even a question from an inspector.
Speedy Petey