1 members (Scott35), 414 guests, and 29 robots.
#23565 03/20/03 11:27 PM
I was asked to do some work for a school and I noticed 9" christy box's with lids marked ground near the back. Is there a code for a dedicated ground rod for each modules subpanel?
#23566 03/21/03 02:51 AM
Sparky*62,
What is a Christy box?, let alone a 9" one.
#23567 03/21/03 04:15 AM
Sounds like you are describing "Hand-Holes" for access / verification of the Clamps and GEC at the rod(s).
Is this correct???
Seen a couple places which had redundant ground rods for supplimental electrodes, and they were driven outside of the gear room (and ended up in the finished sidewalk - resulting in round "Hand-Holes").
These had covers with the phrase:
"Ground Rod", "Grounding Electrode" (or something similar) imbossed on them.
Scott35
#23568 03/21/03 05:04 AM
Here you go Trumpy www.christyconcrete.com
[This message has been edited by joeh20 (edited 03-21-2003).]
Lighting the way
#23569 03/21/03 12:04 PM
sparky*62
When you say modules are you referring to modular (portable) classrooms? If so then a grounding electrode system is required for each module since each module is considered a separate building. See 250.32
Curt
Curt Swartz