I was asked to do some work for a school and I noticed 9" christy box's with lids marked ground near the back. Is there a code for a dedicated ground rod for each modules subpanel?
Sparky*62,
What is a Christy box?, let alone a 9" one.
Sounds like you are describing "Hand-Holes" for access / verification of the Clamps and GEC at the rod(s).
Is this correct???
Seen a couple places which had redundant ground rods for supplimental electrodes, and they were driven outside of the gear room (and ended up in the finished sidewalk - resulting in round "Hand-Holes").
These had covers with the phrase:
"Ground Rod", "Grounding Electrode" (or something similar) imbossed on them.
Scott35
Here you go Trumpy
www.christyconcrete.com [This message has been edited by joeh20 (edited 03-21-2003).]
sparky*62
When you say modules are you referring to modular (portable) classrooms? If so then a grounding electrode system is required for each module since each module is considered a separate building. See 250.32