0 members (),
504
guests, and
20
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2002
Posts: 16
OP
Member
|
Dear Friends, Can somebody throw light on the following. For Standby (Emergency) Diesel engine set and ATS , is their any compulsory time schedule like weekly , monthly etc for load test to keep it 'work" worthy or is it just a matter of one's convenience ?? We have at our site CATERPILLAR make genset of capacities ranging between 250 to 2000 KVA.,for which normally we do a weekly trial run without load for about 5 to 10 minutes( not thro ATS).
|
|
|
|
Joined: Dec 2001
Posts: 300
Member
|
For helthcare facilities in most states, running tests are required weekly and load tests are required monthly.
I believe this is from one title of the NFPA but I don't know where. Monday, I'll try to find the reference.
I don't know about any other industry.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
As maintenanceguy said you may have specific requirments.
Other then that I would suggest you talk to a Cat service guy.
IMHO 5 to 10 minutes is not enough to even reach running temp.
I would be thinking weekly 10 to 15 minutes after hitting the normal operating temp. this forces any water condinsation out of the oil.
Do you have a service contract on these units?
We install many gen sets and when the tech comes out to do the start up they always set the exersise clock for weekly but I do not remember the lenth of run time.
Bob
[This message has been edited by iwire (edited 01-19-2003).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
Maybe http://www.cat.com/ can give you the closest contact person?
|
|
|
|
Joined: Mar 2002
Posts: 582
Member
|
Is the gen arranged for compliance with Article 700, 701 or 702? The requirmeents will be different.
Ron
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Ron, All I find is 700.4 (B) and 701.5 (B) tested in a manner acceptable to the AHJ, nothing in 702
I would think following the makers recommendations would be in a manner acceptable to the AHJ.
Is there something I am missing? Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2002
Posts: 582
Member
|
Most AHJ's enforce NFPA 110. Article 700 and 701 are considered Level 1, and 702 is Level 2. Hospitals are also special. NFPA 110, Chapter 8 goes through the routine maintenance for the two levels.
Ron
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Ok, I missed a FPN to go NFPA 110-1999 Standards for Emergency and Standby Power Systems.
I should look harder before I post.
Bob
[This message has been edited by iwire (edited 01-19-2003).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Posts: 3,682
Joined: October 2000
|
|
|
|