Cindy Offline OP
for working clearances do you use the 150v+ row in the 110.26 table for 208v and 240v ?
#19036 12/19/02 12:03 AM
No, you use 0-150V. Notice it says "nominal voltage to ground." 208 and 240V systems are 120V to ground (nominal)
#19037 12/19/02 09:29 AM
gq Offline
I cant beleve how many get this wrong ontests.I know sme who dont agree with Nick. can 240 go throgh you to ground?
#19038 12/19/02 10:34 AM
Becareful if the 240 is 120/240 4 wire delta. Then the voltage to ground is 208.
Don
Don(resqcapt19)
#19039 12/19/02 08:45 PM
Thanks, good point Don.