Posted By: Cindy 208v & 240v - 12/19/02 03:51 AM
for working clearances do you use the 150v+ row in the 110.26 table for 208v and 240v ?
Posted By: Nick Re: 208v & 240v - 12/19/02 04:03 AM
No, you use 0-150V. Notice it says "nominal voltage to ground." 208 and 240V systems are 120V to ground (nominal)
Posted By: gq Re: 208v & 240v - 12/19/02 01:29 PM
I cant beleve how many get this wrong ontests.I know sme who dont agree with Nick. can 240 go throgh you to ground?
Posted By: resqcapt19 Re: 208v & 240v - 12/19/02 02:34 PM
Becareful if the 240 is 120/240 4 wire delta. Then the voltage to ground is 208.
Don
Posted By: Nick Re: 208v & 240v - 12/20/02 12:45 AM
Thanks, good point Don.