ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 174 guests, and 29 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Feb 2003
Posts: 939
F
Member
I almost overlook that you guys are from Cananda area but true i understand that with multi speed motors it can be treated as seperated circuit but IMO i may disagree with you for a sec so bear with me a min.

speaking of the numbers of circuits going to the equmentit which it will be used and any motor or device need to be service it must have a disconnect switch if not in sight of power source IE. breaker box or MCC or Motor starter contractor assambley. [ i am not sure if your in sight of disconnect switch limited to 25 Metres? correct me if i am wrong here ]

and for that equment it should able disconnect the power simuiotaly [ sp ]

normally in USA verison for 2 speed motors[ 2 winding type ] normally 6 pole disconnect switch will serve the purpose here

[ ditto the European area as well ]

Merci, Marc

Last edited by frenchelectrican; 11/02/07 01:08 AM. Reason: add wording "winding"

Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Joined: Jan 2003
Posts: 174
B
Member
Well if you look at rule 28-812 it states in part that [Quote] Each multi-winding motor and its control equipment shall be provided with disconnecting means in accordance with Rules 28-600 to 28-604[End Quote] and rules 28-602(a)(b)(c)(f) all state that they must be in compliance with 14-010(b)

frenchelectrican: (quote)[ i am not sure if your in sight of disconnect switch limited to 25 Metres? correct me if i am wrong here (end quote)
Very similar here Marc except that it is 9 meters instead of 25.



Joined: Feb 2003
Posts: 939
F
Member
ok Thanks for getting me starght on this one with your codes.

smile

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Joined: May 2007
Posts: 2
R
New Member
Yes they do have to be in compliance with 14-010 (b), but that refers to the point of supply, not at the motor,

Page 2 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5