Posted By: wacked two disconnects on motor - 10/31/07 02:08 AM
I was working on a rooftop exhaust system that has a single motor with two speeds ( high and low ) To my surprise it also has two disconnects one for low and one for high. I would think that one disconnect would be the normal approach except the highlow speed switching control for this is inside on the floor below as is the source of power. The disconnects that are there I presume disconnect the high and low speed winding from their power source. Anybody ever see this before? I was just thinking of the safety concern, if one didn't know about the second disconnect anybody could be working on this motor thinking it is safe to do so but in reality.....gotta check the code book on this one.
Posted By: leland Re: two disconnects on motor - 10/31/07 02:45 AM
NOPE! Not right. A disconnect should disconnect all.

I have never seen this, and I work with alot of theses 2 speed fans. Big acident waiting to happen.
Posted By: frenchelectrican Re: two disconnects on motor - 10/31/07 02:56 AM
For the two speed motor[s] there is a 6 pole disconnect switch avabile on the market but it not cheap what i heard but can order it.

most 2 speed motors useally have 2 set of 3 Ø lines at the motors

Merci, Marc
Posted By: wire_twister Re: two disconnects on motor - 10/31/07 11:19 AM
I agree with Marc, the factory I used to work in had several two speed fans on cooling towers and ac units, and they all had 6 pole disconnects on them. The contactors for all these were inside the building a good ways away from the motors.
Posted By: crash Re: two disconnects on motor - 11/01/07 12:24 AM
Have a look at Section 0 of the CEC (Object, Scope, Definitions). The 2nd phrase in the definition for "Disconnecting means" states that a group of devices [more than one] can serve as a disconnect.
Posted By: bigrockk Re: two disconnects on motor - 11/01/07 04:40 PM
BUT:
Also have a look at 28-602, which refers you back to 14-010(b)
which states :
Manually operable control devices which will safely disconnect all ungrounded conductors of the circuit at the point of supply simultaneously, except for multi-wire branch circuits that supply only fixed lighting loads or non-split receptacles, and that have each lighting load or receptacle connected to the neutral and one ungrounded conductor; and
Posted By: crash Re: two disconnects on motor - 11/02/07 12:02 AM
But read carefully.

"disconnect all ungrounded conductors of a circuit", not "all ungrounded conductors of a motor".

A two speed one winding consequent pole motor would obviously be considered one circuit. But a two speed two winding motor, since it has one set of windings for low speed and a completely different and seperate set of windings for high speed could be considered by the AHJ as having two circuits.
Posted By: wacked Re: two disconnects on motor - 11/02/07 02:26 AM
A quick look at apprndix B (page 357) defining a circuit. To me, this seems to say that this is still just one circuit, this gives some validation to rule 14-010 (b) for which a single multipole switch should have been installed. I guess it all may depend on the weight each section of the code has on each particular topic. Perhaps this is one situation that would need clarification by the inspection branch...any inspectors out there???
Posted By: bigrockk Re: two disconnects on motor - 11/02/07 03:55 AM
Crash you make a good point, I never really thought about it as two totally separate circuits.
With that being said I agree with Wacked that the answer may lie in the definition of a circuit as it applies to the CEC.

This excerpt from the 18th edition handbook may help to shed some light on the intent of the rule, I think the key words here is "All circuits AND apparatus"

We intend that all circuits and apparatus also be provided with manually operable control devices or disconnects that are capable of disconnecting all ungrounded conductors simultaneously at their point of supply. However, we intend that multi-wire branch circuits that supply only fixed lighting loads or non-split receptacles be allowed to be controlled by separate single-pole disconnects in each of the ungrounded conductors of the circuit. In this case, we intend that the loads be connected only to the neutral and one ungrounded conductor (see Figure 14-010).
Posted By: rayc Re: two disconnects on motor - 11/02/07 04:57 AM
If you look at rule 28-812 it states that in a multi winding motor each winding shall have a disconnecting means, it does not really say it has to be one disconnect or two although I do belive one 6 pole is a lot safer and I do not think that 14-010 (b)really applies in this case because it is refering to the point of supply. Just my thoughts
Posted By: frenchelectrican Re: two disconnects on motor - 11/02/07 05:07 AM
I almost overlook that you guys are from Cananda area but true i understand that with multi speed motors it can be treated as seperated circuit but IMO i may disagree with you for a sec so bear with me a min.

speaking of the numbers of circuits going to the equmentit which it will be used and any motor or device need to be service it must have a disconnect switch if not in sight of power source IE. breaker box or MCC or Motor starter contractor assambley. [ i am not sure if your in sight of disconnect switch limited to 25 Metres? correct me if i am wrong here ]

and for that equment it should able disconnect the power simuiotaly [ sp ]

normally in USA verison for 2 speed motors[ 2 winding type ] normally 6 pole disconnect switch will serve the purpose here

[ ditto the European area as well ]

Merci, Marc
Posted By: bigrockk Re: two disconnects on motor - 11/02/07 05:31 AM
Well if you look at rule 28-812 it states in part that [Quote] Each multi-winding motor and its control equipment shall be provided with disconnecting means in accordance with Rules 28-600 to 28-604[End Quote] and rules 28-602(a)(b)(c)(f) all state that they must be in compliance with 14-010(b)

frenchelectrican: (quote)[ i am not sure if your in sight of disconnect switch limited to 25 Metres? correct me if i am wrong here (end quote)
Very similar here Marc except that it is 9 meters instead of 25.


Posted By: frenchelectrican Re: two disconnects on motor - 11/02/07 05:40 AM
ok Thanks for getting me starght on this one with your codes.

smile

Merci, Marc
Posted By: rayc Re: two disconnects on motor - 11/09/07 05:38 AM
Yes they do have to be in compliance with 14-010 (b), but that refers to the point of supply, not at the motor,