Hi folks, I will be installing a new meter main and am using the existing meter main as a sub panel. Besides the obvious separate the grounding bar from the neutral bar, install a new GEC from the new panel, can the existing meter location be covered with a clear cover? Or the existing metermain be replaced with a regular subpanel? Does the NEC address this or it a local AHJ decision?
Thank you Edward
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
Either you reach a higher point today, or you exercise your strenght in order to be able to climb higher tomorrow. Friedrich Nietzsche
Last edited by Niko; 03/29/07 09:55 PM. Reason: i tried to add as a signature.but went in as a reply
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
Neutral (grounded conductor) will be bonded in the old meter socket. As an inspector I would not allow it. Alan--
Alan-- If it was easy, anyone could do it.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
I assume he is saying he will bypass or remove the meter connections and only use the disconnect with the cabinet as a J box. If he can isolate the bonding that should not be an issue but I still would question the suitability of the cover with nothing but that plastic "snap in" over the meter hole. They tend to fall apart pretty fast in the sun. If you screwed a metal cover over the hole I would not be too concerned.
Greg Fretwell
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
Thank you for the replies, Alan, i will isolate (unbond) the grounding and the grounded. My only concern is the meter location and as suggested i may install a metal cover VS clear plastic.