1 members (Scott35), 103 guests, and 11 robots.
#161065 03/29/07 09:49 PM
Niko Offline OP
Hi folks,
I will be installing a new meter main and am using the existing meter main as a sub panel. Besides the obvious separate the grounding bar from the neutral bar, install a new GEC from the new panel, can the existing meter location be covered with a clear cover? Or the existing metermain be replaced with a regular subpanel?
Does the NEC address this or it a local AHJ decision?
Thank you
Edward
Niko #161067 03/29/07 09:54 PM
Niko Offline OP
Either you reach a higher point today, or you exercise your strenght in order to be able to climb higher tomorrow.
Friedrich Nietzsche
Last edited by Niko; 03/29/07 09:55 PM. Reason: i tried to add as a signature.but went in as a reply
Niko #161193 03/31/07 11:36 AM
Neutral (grounded conductor) will be bonded in the old meter socket. As an inspector I would not allow it.
Alan--
Alan--
I assume he is saying he will bypass or remove the meter connections and only use the disconnect with the cabinet as a J box. If he can isolate the bonding that should not be an issue but I still would question the suitability of the cover with nothing but that plastic "snap in" over the meter hole. They tend to fall apart pretty fast in the sun. If you screwed a metal cover over the hole I would not be too concerned.
Niko #161217 03/31/07 03:33 PM
Niko Offline OP
Thank you for the replies,
Alan, i will isolate (unbond) the grounding and the grounded.
My only concern is the meter location and as suggested i may install a metal cover VS clear plastic.