0 members (), 402 guests, and 24 robots.
Page 3 of 3 1 2 3
#14309 09/19/02 11:58 PM
Looks good to me except for maybe the distance from the window to the P.O.A.
But, if the poco didn't have a problem with it who am I to complain. Just hope the future tennants don't use the tri-plex as a clothes line [Linked Image].
If it were me, I would have tried to get above the windows but I don't know the particulars of the job.
And I thought that I was the only one that used plastic bushings on PVC... did it for years.
Looks good!
#14310 09/20/02 12:40 AM
Article 100 Page 4 of 9
General
Grounding Electrode Conductor
The definition for “Grounding Electrode Conductors” was revised to read:
Grounding Electrode Conductor. The conductor that connects the grounding electrode to the grounded (neutral) conductor at service equipment [250.24(A)], source of a separately derived system [250.30(A)(2)], or to the equipment grounding conductor at each building or structure disconnect that is supplied by a feeder [250.32(E)].
I did not get as think so badly as you shocked I did.
#14311 09/20/02 12:53 AM
Would not the Service Disconnect be considered part of the Service Equipment?
But I like the way you think, Sean!
-Virgil
5 Star Inspections
Member IAEI
#14312 09/20/02 01:32 AM
as well as the meter
#14313 09/20/02 01:37 AM
Hmmmm... I might just have to let Tom or Master66 he'p me out on this one!
You're gonna fit in well here, Sean!
-Virgil
5 Star Inspections
Member IAEI
#14314 09/20/02 05:47 AM
Sparky, I had wondered about the bonding issues with the min-Es on PVC (it is PVC). What do you think?
well i've been busted on it before.... the rationale being mini-Es are not listed for pvc, and do not allow for the pvc to expand/contract. Bonding would follow the definition of 'fitting' vs. 'fastener'......
(please don't go there, or we'll be bonding #100 staples too...) [Linked Image]
in my case i had 4-500kcmil's in 4" sch 80, and used beeline hangers every 30" , the AHJ let it go.....after i bemoaned the wieght of the riser vs. cheesy 4" two hole straps or quickclips..... [Linked Image]
(methinks a similar thread ran a yr or so ago on this?)
as to the definitional application of 'pipe hanger' , i have no white book reference
(or can't find one) ..... my god, we're the nitpickyest trade! [Linked Image]
anyhow,
your truely the Tom Cruise of the industry, carry on!
( you DID wear all black & a ski mask doing this right?) [Linked Image]
#14315 09/20/02 07:07 AM
In response to a few posts here, the way i am reading the NEC the gec must be connected to the service at the service disconnecting means which would not be the meter. 250.24 a 1. I also do not believe the meter is part of the "service equipment" as defined by the NEC.
[This message has been edited by Electricmanscott (edited 09-20-2002).]
#14316 09/20/02 09:19 AM
Scott,
250.24(A)(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
Some argue that the meter is not accessible, but I think that it is, its just not readily accessible.
Don
#14317 09/21/02 12:34 AM
I stand corrected. 230.66 clears that up
carry on........ LOL
Page 3 of 3 1 2 3