1 members (Scott35), 565 guests, and 35 robots.
Tom,
Frank said he has 22 fixtures, not 44.
Ed
Ed,
What Tom did is put fixture 1 on phases A&B, fixture 2 on B&C, fixture 3 on A&C, and so on. This will give you 15 connections to A and B and 14 connections to C.
Don
The current drawn by a fixture on phases A and B is not "in phase with" the current drawn by a fixture on phases B and C. They won't both be at "maximum" at the same time. They add, but it would be vectorially.
That's why I would recommend the volt-amp calculation.
ED
[This message has been edited by electric-ed (edited 09-12-2002).]
Tom Offline
Ed,
I don't quite see the point about about fixtures on A & B not being in phase with fixtures on B & C. The load on B phase will be twice the load on either A or C phase if you have one fixture connected A&B and one fixture connected B&C.
Working with volt-amps may be meaningful for calculating a transformer load, but in this case, I think the higher number is the correct one to use.
The use of amps in the calculation may be a code requirement if I'm reading things right. In the following order 220.10, 220.3(B)(2) .
Of course, I could be just plain stubborn here, after all, that's in the job description of "electrician." [Linked Image]
[This message has been edited by Tom (edited 09-13-2002).]