Little League Baseball Field - 09/11/02 08:27 PM
Please check my math:
(22) 1500 watt metal halide light standard fixtures @208 volts, 8.2 amps each. They will be balanced on a 120/208 volt, three phase, 4 wire service.
37,523 watt load divided by 208 x 1.73=104 amps.
The load would be considered continuous thus multiply by 1.25 = 130 amps total load.
Am I correct?