Please check my math:

(22) 1500 watt metal halide light standard fixtures @208 volts, 8.2 amps each. They will be balanced on a 120/208 volt, three phase, 4 wire service.

37,523 watt load divided by 208 x 1.73=104 amps.
The load would be considered continuous thus multiply by 1.25 = 130 amps total load.

Am I correct?