ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 526 guests, and 29 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 3 of 3 1 2 3
#114224 02/10/03 04:46 PM
Joined: Jun 2002
Posts: 58
E
Member
Forget scraping paint! That's a concentric knockout hole, so you have to use an Eq. Bond. Conductor, and appropriate bonding fitting.

#114225 03/17/03 01:25 AM
Joined: Mar 2003
Posts: 1
T
Junior Member
I'm not sure it is a fitting at all. It could be we're seeing the material that the panel itself is mounted to, and what has been cut off is EMT. ?

#114226 04/02/03 04:28 PM
Joined: Mar 2003
Posts: 36
U
Member
Back to the nylon cable ties for a minute. Have any of you out there come behind on a project where these were installed, with the tails cut off with a dykes or Kleins and done minor surgery on your hands and forearms? I know of an electrician that required stiches to close the would produced by one of these short tails.

#114227 04/02/03 04:41 PM
Joined: Aug 2002
Posts: 1,691
S
Member
Quote
Have any of you out there come behind on a project where these were installed, with the tails cut off with a dykes or Kleins and done minor surgery on your hands and forearms?

A good practice is probably to turn the tie so the little "buckle" faces the rear of the panel before tightening it all the way.

That way all sharp edges are nowhere near someone's fingers.

#114228 05/29/03 05:35 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Don't know if anyone is still reading old posts.... But reguardless of the connector, this is a three phase residential service?

Now the zip tie thing. Up here, ( San Fran )310-15 is required. Not just for that piece of plumbing nipple they ran through, but the zip tie too!


Mark Heller
"Well - I oughta....." -Jackie Gleason
#114229 05/30/03 04:50 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
e57, 310.15 does not apply to bundles less than 24" in length, most times in a panel you would not exceed this, are they making you apply this for all lengths?


Quote
2002 NEC

310.15(B)(2) Adjustment Factors.

(a) More Than Three Current-Carrying
Conductors in a Raceway or Cable.


Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(2)(a).


[This message has been edited by iwire (edited 05-30-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#114230 05/31/03 02:01 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
To iwire:

Exactly! From what little we can see from this picture, ( I figure this to be a Meter / Main with distriution. 12/24 100 - 200a Breakers in a single row up one side.) The conductors could be easily be more than 24".

And, the conduit "could" run half way through the house. From the picture alone we really can't tell.

I just figured I would chime in on those upset about zip tie knicks. Maybe just iliminate them?

And, I think the original point was that none of these circuits have a viable ground.


[This message has been edited by e57 (edited 05-31-2003).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
#114231 06/04/03 07:42 PM
Joined: May 2003
Posts: 2
S
Junior Member
If this "connector" wasn't 1" tradesize, I'd say it was an airduct sampling tube cut off just past the flange. The notches on the flange aren't really deep enough either to support this theory, but perhaps it's something similar. Probably a work-around for not having the proper tool to make room in the masonary for a 1" connector. I'm assuming the enclosure is mounted to masonary by looking at the tapcon, but who knows, perhaps this assumption is also unfounded. In any case, it's clearly not street legal!

[This message has been edited by Surge (edited 06-04-2003).]

#114232 06/14/03 11:29 PM
Joined: Jun 2003
Posts: 681
P
Member
Maybe that is 'METALLIC COATED PVC WITH A NEW SNAPIN CONNECTOR' (doesn't require a ground)
I am sure you have all seen one, they are very common, they are UL listed under the code letters CRAP.

Pierre


Pierre Belarge
#114233 06/16/03 01:43 AM
Joined: May 2003
Posts: 1,158
Member
Could it be a reducing washer with some kind of thin wall tubing maybe not emt but something else?