Jon & Tom understand I have no inside knowledge on this subject and do not have the option of using this table at my job.
You both bring up some interesting points to think about, the problem I have is there is nothing in that article that talks about diversity.
Another problem I have is if you calculate the loads for both panels in the same way it will not make a difference.
As an example a subpanel sized to feed only two outside air conditioner compressor condenser units.
They both have a minimum circuit ampacity of 50 amps, we install a 100 amp subpanel using Table 310.15(B)(6) which requires 4 AWG CU with 75 C or 90 C conductors.
This panel at most see a load of 80 amps, as the tag on the HVAC units already includes the 125% increase required by 440.
310.16 lists 4 AWG CU @ 75 C as 85 amps, so how would this be a problem?