1. Security system, dedicated circuit
A1)210.8(A)(5) Exception #3
2. Satellite TV distribution system
A2)May meet 210.8(A)(5) Exception #2
3. Satellite Internet service distribution center w/wireless network
A3)May meet 210.8(A)(5) Exception #2
4. Water softener, dedicated circuit
A4)210.8(A)(5) Exception #2
5. Three double-duplex general use recepts on GFI CB. Inspector wants GFI feed-thru outlet in first box.
A5)Code does not specify type of GFCI protection required.
6. Five duplex on GFI CB.
A6)Code does not specify type of GFCI protection required.
7. Sump pump, dedicated circuit, no GFI. A7)210.8(A)(5) Exception #2
8. Central Vacuum system, dedicated circuit, no GFI.
A8)210.8(A)(5) Exception #2
9. One double duplex for two treadmills and TV. Booklets say no GFI for treadmills.
Inspector wants TV removed from recpts supplying treadmills and placed on GFI circuit.
A9)This circuit does not meet any of the exceptions and requires GFCI protecion. The manufacturer's instructions not to use GFCIs does not change the code rule.
Note that where Exception #2 is used only a single receptcle is permitted. If the installed receptacle is a duplex, then GFCI protection is required.
Don
[This message has been edited by resqcapt19 (edited 12-22-2004).]