You can put 9 THHN, 14 or 12 AWG current carrying conductors in a raceway before derating becomes an issue.

310.16 shows 14 AWG THHN rated 25 amps

Table 310.15(B)(2)(a) shows a 70% downward adjustment for 7 to 9 current carrying conductors

25 amps x .7 = 17.5 amps

The 14 AWG is still OK for a 15 amp breaker.

For 12 AWG

310.16 shows 12 AWG THHN rated 30 amps

30 amps x .7 = 21 amps.

The 12 AWG is still OK for a 20 amp breaker.

There are areas that must use EMT for residential.

For derating purposes you can use the 90 C column of 310.16 if you use THHN.