440.12(A)(1) really makes it sound like you size the disconnect to 115% of the 65.68a on the nameplate.
That is the branch circuit selection current.

Quote
(1) Ampere Rating. The ampere rating shall be at least 115 percent of the nameplate rated-load current or branch-circuit selection current, whichever is greater.


Greg Fretwell