Minimum circuit ampacity is used to size the conductors, MOCP sizes the breaker.
You can end up with some scary looking combinations but thus is the norm when you are working with motors.
In your case you could use #4 cu and a 110a breaker
That ".68a" pushed you over from #6


Greg Fretwell