When I wear my inspector hat, I enforce the intent of the code, not just what is written. The codes as written at least the NEC in the US, is to be consider the absolute minimum to be safe. It even states that code is not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use (Yes I plagerized. Sue me
For example, a sparkie puts a 120 volt pump 500 feet from the panel, uses a 20 amp breaker and #12 wire. Is it a violation of the code as written? Nope. Will I red tag it? If I could not get the right answer out of the electrican, you bet. As an inspector, it is your job to protect the ones you serve. If the contractor is dumb enough, to install it, he will likely fight it. There are standards and exceptable practices, building and now even energy codes coming into play when inspecting too that will back you up. I do believe that voltage drop will finally become a code issue, not just a standard or specification here in the future.
When I wear my elctrician hat, I install in a manner where my work does not need to be scuntinized. I do not try to place a staple exactly at 12 inches from a box nor do I try to hit 4 1/2 feet after that. Not to boast, when you look at my work, there is no guessing if it is to code or not, ever to a code nazi, as someone put it on this board.
My conduit straps are rearly at 10 feet. If they are, I can gurantee that you can tell at any distance they are 10 feet apart. This is a another good example. If a emt conduit is supported at every 9 1/2 feet, can it be red tag for lack of support? The code states not to exceed 10 feet.