I would start by checking your voltage at the panel. Check one leg to ground (120), then the other to ground (120), and finally both to each other (240). Then check each individual circuit breaker. If all that checks out, then I would locate the branch circuit that's giving u the problem and shut that breaker off. Only then would I start removing devices to check for good terminations. Probably a stab-lock somewhere, lol.